Z tego co pamiętam to błędy te które są w kodzie powinny być wyświetlane w zakładce Current fault, fault 1, fault 2 i fault 3.
Witam.
Podłączyłem moje Rotenso Aquami modułem USR-DR404 WIFI TCP <=> Modbus RTU .
Do pliku configuration.yaml dodałem ten wiersz modbus: !include modbus.yaml i plik modbus.yaml a w nim:
- name: rotenso
type: tcp
host: 192.168.0.101
port: 502
delay: 5
timeout: 2
switches:
- name: heatpump_on_off_toggle
unique_id: heatpump_on_off_toggle
slave: 1
address: 0
write_type: holding
command_on: 2
command_off: 0
verify:
input_type: holding
address: 0
state_on: 2
state_off: 0
sensors:
- name: heatpump_Fan_Speed
unique_id: heatpump_Fan_Speed
scan_interval: 5
address: 102
state_class: measurement
slave: 1
scale: 1
input_type: holding
unit_of_measurement: r/min
- name: heatpump_flow_rate
unique_id: heatpump_flow_rate
scan_interval: 5
address: 138
state_class: measurement
slave: 1
scale: 0.01
precision: 3
input_type: holding
unit_of_measurement: m3/h
- name: heatpump_power_state
unique_id: heatpump_power_state
address: 0
scan_interval: 5
slave: 1
- name: heatpump_temperature_C1
unit_of_measurement: °C
state_class: measurement
unique_id: heatpump_temperature_C1
scan_interval: 5
address: 2
slave: 1
offset: 0
scale: 1
- name: heatpump_temperature_TW_IN
unit_of_measurement: °C
state_class: measurement
unique_id: heatpump_temperature_TW_IN
scan_interval: 5
address: 104
slave: 1
offset: 0
scale: 1
- name: heatpump_temperature_TW_OUT
unit_of_measurement: °C
state_class: measurement
unique_id: heatpump_temperature_TW_OUT
scan_interval: 5
address: 105
slave: 1
offset: 0
scale: 1
- name: heatpump_condensor_temperature_T3
unit_of_measurement: °C
state_class: measurement
unique_id: heatpump_condensor_temperature_T3
scan_interval: 5
address: 106
slave: 1
offset: 0
scale: 1
- name: heatpump_outdoor_temperature_T4
unit_of_measurement: °C
state_class: measurement
unique_id: heatpump_outdoor_temperature_T4
scan_interval: 5
address: 107
slave: 1
offset: 0
scale: 1
- name: heatpump_exhaust_gas_temperature_Tp
unit_of_measurement: °C
state_class: measurement
unique_id: heatpump_exhaust_gas_temperature_Tp
scan_interval: 5
address: 108
slave: 1
offset: 0
scale: 1
- name: heatpump_suction_temperature_Th
unit_of_measurement: °C
state_class: measurement
unique_id: heatpump_suction_temperature_Th
scan_interval: 5
address: 109
slave: 1
offset: 0
scale: 1
- name: heatpump_refrigerant_liquid_side_temperature_T2
unit_of_measurement: °C
state_class: measurement
unique_id: heatpump_refrigerant_liquid_side_temperature_T2
scan_interval: 5
address: 112
slave: 1
offset: 0
scale: 1
- name: heatpump_refrigerant_liquid_side_temperature_T2B
unit_of_measurement: °C
state_class: measurement
unique_id: heatpump_refrigerant_liquid_side_temperature_T2B
scan_interval: 5
address: 113
slave: 1
offset: 0
scale: 1
- name: heatpump_total_water_outlet_T1
unit_of_measurement: °C
state_class: measurement
unique_id: heatpump_total_water_outlet_T1
scan_interval: 5
address: 110
slave: 1
offset: 0
scale: 1
- name: heatpump_Operating_frequency_Hz
unit_of_measurement: Hz
unique_id: heatpump_Operating_frequency_Hz
scan_interval: 5
address: 100
slave: 1
offset: 0
scale: 1
- name: heatpump_Power
unit_of_measurement: kW
unique_id: heatpump_Power
device_class: power
scan_interval: 5
address: 140
state_class: measurement
slave: 1
scale: 0.01
offset: 0
precision: 3
- name: heatpump_PMV
unit_of_measurement: P
unique_id: heatpump_PMV
device_class: energy
scan_interval: 5
address: 103
state_class: total_increasing
slave: 1
- name: heatpump_high_pressure
unit_of_measurement: kPa
unique_id: heatpump_high_pressure
scan_interval: 5
address: 116
slave: 1
offset: 0
scale: 1
- name: heatpump_low_pressure
unit_of_measurement: kPa
unique_id: heatpump_low_pressure
scan_interval: 360
address: 117
slave: 1
offset: 0
scale: 1
- name: heatpump_total_climate_curve
unit_of_measurement: °C
state_class: measurement
unique_id: heatpump_total_climate_curve
scan_interval: 5
address: 136
slave: 1
offset: 0
scale: 1
- name: heatpump_operating_current
unit_of_measurement: A
unique_id: heatpump_operating_current
device_class: energy
scan_interval: 5
address: 118
state_class: total_increasing
slave: 1
scale: 1
offset: 0
precision: 3
- name: heatpump_Compressor_operation_time
unit_of_measurement: h
unique_id: heatpump_Compressor_operation_timet
device_class: energy
scan_interval: 360
address: 122
state_class: total_increasing
slave: 1
scale: 1
offset: 0
precision: 3
- name: heatpump_128
unique_id: heatpump_128
address: 128
scan_interval: 5
slave: 1
input_type: holding
- name: heatpump_129
unique_id: heatpump_129
address: 129
scan_interval: 5
slave: 1
input_type: holding
- name: heatpump_electricity_consumption
unique_id: heatpump_electricity_consumption
address: 143
slave: 1
data_type: int32
scan_interval: 60
unit_of_measurement: kWh
device_class: energy
state_class: total_increasing
input_type: holding
- name: heatpump_Power_output
unique_id: heatpump_Power_output
address: 145
slave: 1
data_type: int32
unit_of_measurement: kWh
device_class: energy
state_class: total_increasing
scan_interval: 60
input_type: holding
climates:
- name: heatpump_climate
unique_id: heatpump_climate
address: 110
slave: 1
input_type: holding
max_temp: 50
min_temp: 25
precision: 1
scale: 1
target_temp_register: 136
temp_step: 1
temperature_unit: °C
write_registers: true
hvac_mode_register:
address: 1
values:
state_auto: 1
state_cool: 2
state_heat: 3
- name: Górna temp. krzywej 9
unique_id: gorna_temp_krzywej_9
address: 265
data_type: int16
input_type: holding
max_temp: 60
min_temp: 25
offset: 0
precision: 1
scale: 1
target_temp_register: 265
temp_step: 1
temperature_unit: C
hvac_mode_register:
address: 0001
values:
state_heat: 3
- name: Dolna temp. krzywej 9
unique_id: dolna_temp_krzywej_9
address: 266
data_type: int16
input_type: holding
max_temp: 60
min_temp: 25
offset: 0
precision: 1
scale: 1
target_temp_register: 266
temp_step: 1
temperature_unit: C
hvac_mode_register:
address: 0001
values:
state_heat: 3
- name: Dolna temp. zewn. krzywej 9
unique_id: dolna_temp_zewn_krzywej_9
address: 268
data_type: int16
input_type: holding
max_temp: 30
min_temp: -25
offset: 0
precision: 1
scale: 1
target_temp_register: 268
temp_step: 1
temperature_unit: C
hvac_mode_register:
address: 0001
values:
state_heat: 3
- name: Górna temp. zewn. krzywej 9
unique_id: gorna_temp_zewn_krzywej_9
address: 267
data_type: int16
input_type: holding
max_temp: 30
min_temp: -25
offset: 0
precision: 1
scale: 1
target_temp_register: 267
temp_step: 1
temperature_unit: C
hvac_mode_register:
address: 0001
values:
state_heat: 3
Problem polega na tym że się nie znam i nie wiem jak odczytywać i zapisywać pojedyncze bity .NP: informacja o defroście jest na adresie 129 BIT15 ?
I termostat nie działa - na krzywej pokazuje dobrze jak wyłączę krzywą to jest 255 stopni i nie zmienia temperatury
Ogarnąłeś integrację pompy z HA po modbus.Szukam informacji jak to podpiąć i skonfigurować?Pamiętasz może gdzie podpinałeś się konwerterem pod które wejscia masz moze jakies fotki.Podpinałeś pod płyte czy do sterownika.
Jak to wszystko skonfigurować.Znalazłem konwerter w szufladzie ale nie wiem czy będzie ok(elfin ew11).
Posiadam Rotenso Aquami monoblock podłączałem pod sterownik przewodowy
https://forum.arturhome.pl/t/pompa-ciepla-kaisai-po-modbus/15575/3?u=lajosz
Czy bez tych elementow na konicach lini to nie ruszy?(co to) Ja mam elfin11ew i we wtyczce mam zasilanie (+ -) i (A B) nie mam gnd ,c,y moge pod minus elfin podpiac gnd ze sterownika? Czy trzeba jeszcze cos w jednostce aktywowac żeby modbus działał?Luknij na moje ustawienia czy tak to ma być
Narazie podłączylem bez E i bez tych oporniczkow ale w statusie wszedzie 0 wiec chyba brak połączenia.
ustawione?
Jak pisałem zbytnio się nie znam.
W pompie nic nie aktywujesz - działa samo. Te elementy to terminacja Lini - rezystor 120 omów . Możesz podłączyć tylko AiB masa (gdn) nie jest wymagana ale dobrze podłączyć tylko z jednej strony . Mój konwerter zamienia TCP na RTU inaczej trzeba ustawić type: rtuovertcp (chyba) . Ale lepiej jakby wypowiedział się ktoś kto się zna.
jest swiatełko w tunelu
Można na Was liczyć,juz nie pierwszy raz otrzymuję tu pomocną dłoń :
podzielisz sie swoim kodem modbus.yaml i dashbordem ,pewnie bede sobie go modyfikował ale tak by było najszybciej
Modbus.yaml umieściłem wyżej .
Widzę że robisz w NR ja to ogarnąłem inaczej.
Dashbord pewnie nie będzie pasował bo są jeszcze pomocnicy , liczniki zamel i sterowanie zaworem zewnętrznym po modbus . Cop wyliczam template dzieląc moc cieplną wygenerowaną z pompy przez zewnętrzny licznik Zamela
type: grid
cards:
- type: vertical-stack
cards:
- type: thermostat
entity: climate.heatpump_climate
show_current_as_primary: true
- type: gauge
entity: sensor.cop
max: 6
min: 1
needle: true
severity:
green: 3
yellow: 2.4
red: 1.8
- show_name: false
show_icon: true
type: button
entity: switch.heatpump_on_off_toggle
grid_options:
columns: 12
rows: auto
show_state: false
icon_height: 22px
- type: tile
entity: switch.pc_valve1
name: Przepływ co 0,7 -1,1m
icon: mdi:valve
color: accent
show_entity_picture: true
state_content: state
vertical: false
features_position: bottom
- type: tile
entity: binary_sensor.df
icon: mdi:snowflake-alert
color: accent
show_entity_picture: true
hide_state: false
vertical: false
features_position: bottom
- type: tile
entity: binary_sensor.grzalka_3000w
icon: mdi:water-boiler
color: red
show_entity_picture: true
vertical: false
features_position: bottom
- type: vertical-stack
cards:
- type: gauge
entity: sensor.zamel_lew_02_electricity_meter_power_active_phase_1
needle: true
severity:
green: 0.7
yellow: 1.3
red: 2
min: 0
max: 3
grid_options:
columns: 12
rows: auto
unit: kW
name: Moc PC L2
- type: gauge
entity: sensor.heatpump_power
needle: true
severity:
green: 2.9
yellow: 5
red: 6.5
min: 0
max: 10
grid_options:
columns: 10
rows: auto
unit: kW
- type: gauge
entity: sensor.heatpump_operating_current
needle: true
severity:
green: 1
yellow: 4
red: 8
min: 0
grid_options:
columns: 10
rows: auto
max: 13
- type: gauge
entity: sensor.heatpump_operating_frequency_hz
needle: true
severity:
green: 30
yellow: 45
red: 60
min: 0
max: 90
grid_options:
columns: 12
rows: auto
- type: gauge
entity: sensor.moc_pompy_ciepla
needle: true
severity:
green: 0.7
yellow: 1.3
red: 2
min: 0
max: 6
grid_options:
columns: 10
rows: auto
unit: kW
grid_options:
columns: 9
rows: auto
- type: vertical-stack
cards:
- type: gauge
entity: sensor.heatpump_flow_rate
needle: true
severity:
green: 0.6
yellow: 0.9
red: 1.45
min: 0
grid_options:
columns: 10
rows: auto
max: 2
- type: gauge
entity: sensor.heatpump_fan_speed
needle: true
severity:
green: 300
yellow: 200
red: 480
max: 600
grid_options:
columns: 10
rows: auto
min: 0
- type: gauge
entity: sensor.heatpump_high_pressure
needle: true
severity:
green: 800
yellow: 2600
red: 3200
max: 4200
grid_options:
columns: 10
rows: auto
min: 500
- type: gauge
entity: sensor.heatpump_pmv
needle: true
severity:
green: 83
yellow: 112
red: 190
min: 0
max: 480
grid_options:
columns: 10
rows: auto
- type: tile
entity: sensor.heatpump_power_output
vertical: false
features_position: bottom
- type: tile
entity: sensor.zamel_liw_01_electricity_meter_value
vertical: false
features_position: bottom
grid_options:
columns: 9
rows: auto
- type: vertical-stack
cards:
- type: vertical-stack
cards:
- type: gauge
entity: sensor.heatpump_temperature_tw_out_2
needle: true
severity:
green: 34
yellow: 30
red: 44
min: 25
max: 50
grid_options:
columns: 10
rows: auto
- type: gauge
entity: sensor.heatpump_refrigerant_liquid_side_temperature_t2b
needle: true
severity:
green: 40
yellow: 65
red: 80
min: 10
max: 100
grid_options:
columns: 10
rows: auto
- type: gauge
entity: sensor.heatpump_outdoor_temperature_t4
needle: true
severity:
green: 5
yellow: 0
red: 20
min: -15
max: 29
grid_options:
columns: 10
rows: auto
- type: gauge
entity: sensor.heatpump_exhaust_gas_temperature_tp
needle: true
severity:
green: 40
yellow: 65
red: 80
min: 10
max: 100
grid_options:
columns: 10
rows: auto
- type: tile
entity: sensor.heatpump_compressor_operation_time
icon: mdi:clock-check-outline
vertical: false
features_position: bottom
- type: tile
entity: sensor.heatpump_electricity_consumption
vertical: false
features_position: bottom
grid_options:
columns: 9
rows: auto
- type: vertical-stack
cards:
- type: gauge
entity: sensor.heatpump_temperature_tw_in
needle: true
severity:
green: 34
yellow: 30
red: 44
min: 25
max: 50
grid_options:
columns: 10
rows: auto
- type: gauge
entity: sensor.heatpump_refrigerant_liquid_side_temperature_t2
needle: true
severity:
green: 30
yellow: 55
red: 70
min: 0
max: 90
grid_options:
columns: 10
rows: auto
- type: gauge
entity: sensor.heatpump_condensor_temperature_t3
needle: true
severity:
green: 5
yellow: 0
red: 20
min: -15
max: 30
grid_options:
columns: 10
rows: auto
- type: gauge
entity: sensor.heatpump_suction_temperature_th
needle: true
severity:
green: 5
yellow: 0
red: 22
min: -15
max: 30
grid_options:
columns: 10
rows: auto
- type: tile
entity: sensor.heatpump_128
vertical: false
features_position: bottom
- type: tile
entity: sensor.heatpump_129
vertical: false
features_position: bottom
grid_options:
columns: 9
rows: auto
- type: vertical-stack
cards:
- type: custom:gauge-card-pro
entity: sensor.sonoff_basic_r3_pompa_ciepla_aut
use_new_from_segments_style: true
segments:
- from: 25
color: blue
- from: 28
color: red
needle: true
gradient: true
entity2: sensor.heatpump_temperature_tw_out_2
max: 50
min: 25
hide_background: true
tap_action:
action: more-info
primary_value_text_tap_action:
action: more-info
gradient_resolution: high
secondary_value_text_tap_action:
action: more-info
icon_tap_action:
action: more-info
inner:
mode: severity
titles:
primary: "{{ state_attr(entity, 'friendly_name') }}"
- chart_type: line
period: 5minute
type: statistics-graph
entities:
- sensor.heatpump_flow_rate
- sensor.zamel_lew_02_electricity_meter_power_active_phase_1
- sensor.heatpump_power
stat_types:
- mean
days_to_show: 1
min_y_axis: 0
grid_options:
columns: 12
rows: null
fit_y_data: true
logarithmic_scale: false
hide_legend: true
unit: kW
- chart_type: bar
period: day
type: statistics-graph
entities:
- >-
sensor.zamel_lew_02_electricity_meter_total_forward_active_energy_phase_1
- sensor.heatpump_power_output
days_to_show: 30
min_y_axis: 0
grid_options:
columns: 12
rows: null
fit_y_data: true
logarithmic_scale: false
hide_legend: true
stat_types:
- change
- chart_type: bar
period: day
type: statistics-graph
entities:
- sensor.zamel_liw_01_electricity_meter_value
days_to_show: 30
min_y_axis: 0
grid_options:
columns: 12
rows: null
fit_y_data: true
logarithmic_scale: false
hide_legend: true
stat_types:
- change
grid_options:
columns: 12
rows: 11
- type: history-graph
entities:
- entity: switch.pc_valve1
- entity: switch.pc_valve2
- entity: binary_sensor.df
- entity: binary_sensor.grzalka_3000w
- entity: sensor.heatpump_129
- entity: sensor.heatpump_128
grid_options:
columns: 69
rows: auto
- type: tile
grid_options:
columns: 9
rows: 2
entity: climate.gorna_temp_zewn_krzywej_9
vertical: false
tap_action:
action: toggle
features:
- type: target-temperature
features_position: bottom
- type: tile
grid_options:
columns: 9
rows: 2
entity: climate.gorna_temp_krzywej_9
vertical: false
tap_action:
action: toggle
features:
- type: target-temperature
features_position: bottom
- type: statistic
entity: sensor.heatpump_power
period:
calendar:
period: day
stat_type: mean
name: Średnia Dziś
- type: tile
grid_options:
columns: 9
rows: 2
entity: climate.dolna_temp_zewn_krzywej_9
vertical: false
tap_action:
action: toggle
features:
- type: target-temperature
features_position: bottom
- type: tile
entity: climate.dolna_temp_krzywej_9
vertical: false
tap_action:
action: toggle
features:
- type: target-temperature
features_position: bottom
grid_options:
columns: 9
rows: 2
column_span: 10
nie w nodred tylko próbowałem czy jest komunikacja
robię to w yaml
masz racje nie będzie pasował, zrobię po swojemu ,
ale już jest dobrze
jak ogarnę to się pochwałę . Dzięki za pomoc.
Probuje dostosowac swoja stara kartę pompy ciepla diy do nowej york.Jeszcze sporo mi brakuje :stan pracy ,jaki tryb ,ktora krzywa i mozliwosc zmiany,czy praca reczna na salej temp czy z krzywej.Duzo aderesow modbus zwraca jakieś liczby ktore nie wiem za co odpowiadają.Jak ktos ma wieksza wiedzę to moze sie podzieli.Na ta chwile wyglada to tak
Plus do tego termostat zadawania stalelej i 4 termistaty krzywej 9 ktorej nie testiwalem jeszcze.Nue wiem za bardzo o co chodzi z tą krzywą ,te termostaty to temp zadane krzywej 9?
Powoli naprzód ,moze sie uda zrezygnowac calkiem z aplikacji na rzecz HA.Zostały do ogarniecia tryb cichy ,eko .Harmonogramy chyba sobie daruję
Co do krzywej 9 . W sterowniku przewodowym wybierasz krzywą 9 w której sam określasz temperatury wody kotłowej . W HA możesz potem zmieniać , ale po każdej zmianie krzywej pompa się wyłącza trzeba ją włączyć klikając ON w HA.
A czy jest opcja dostania się do odczytu i zmiany w nastawach serwisowych pompy z poziomu HA?
Dzieki pomocy osiągnąłem prawie wszystko co chciałam,jest juz nawet stworzony w HA termostat ze srednich temp w pomieszczeniach i on/off pompy.
Pracuje z trochę wyższą temp niz zakładałem, ale poprawiło to czasy pracy sprężarki i jej przestoje.Krzywa9 jest ,ale pilnuje jeszcze tego termostat . Gdyby ta pompa modulowała do 20Hz pewnie niebyły potrzebny.
Cześć wszystkim. Czy ktoś może podpowiedzieć jak podłączyć termostat pokojowy do pompy Kaisai KMK‑100RY3. Chcę podłączyć się przez ZRS1LN-NCMR na ZigBee.
Dziękuję bardzo za instrukcję. Czy mógłbyś mi napisać do czego mam się podpiąć w tym moim urządzonku ZRS1LN-NCMR. Nie chcę spalić pompy. Z tego co zobaczyłem to w pompie muszę się podpiąć do 3 i 15.
To zależy jak jest skonfigurowana, jeśli nie masz pojęcia co robisz zaproś instalatora, który ją zakładał…
Ta firma która to zakładała za każdą wizytę życzy sobie 500zl. Jeżeli do podpięcia jest tylko kilka przewodów to ogarnę to sam,pod warunkiem że będę wiedział co z czym połączyć. Nie uśmiecha mi się wspierać złodziejskiej firmy,która i tak już na mnie zarobiła kilkadziesiąt tysięcy. Oni mi zakładali wszystko z dotacji. Termostat pokojowy powinni mi od razu zamontować a nie pójść po jak najmniejszym oporze.
To przeczytaj tę instrukcję (ona jest napisana dla ludzi o przeciętnym wykształceniu technicznym, nie dla profesorów), zrozum i zrób.